HabitatSteve
Member
- Location
- Hopkins, MN
- Occupation
- Contractor, electrican
1. Is a switched duplex receptacle (used for a low voltage plug-in lighting transformer) located in the cabinet under the kitchen sink (<6' from the stainless sink edge) required to be GFCI protected and if so, does that location meet the necessary accessible requirements? (All the usual cleaning supplies, etc must be removed to get to it.) Is this an AHJ determination?
2. Does the GFCI installed for a refrigerator (also <6' from the sink edge) meet the necessary accessible requirements if the refrigerator must be pulled out to get to it?
3. Does the duplex receptacle installed for a gas range (behind the range and <6' from the sink edge) need to be GFCI protected and does that location meet the necessary accessible requirements? If it makes any difference, the receptacle is unused because an electric range was (correctly) installed.
Have either of these changed from the 2014 NEC, 2017 NEC, or current 2020 NEC? There is some question as to which code will be applied to a very old, still open, city permit about to be inspected and closed.
These are located in a full kitchen. Code references would probably be helpful.
2. Does the GFCI installed for a refrigerator (also <6' from the sink edge) meet the necessary accessible requirements if the refrigerator must be pulled out to get to it?
3. Does the duplex receptacle installed for a gas range (behind the range and <6' from the sink edge) need to be GFCI protected and does that location meet the necessary accessible requirements? If it makes any difference, the receptacle is unused because an electric range was (correctly) installed.
Have either of these changed from the 2014 NEC, 2017 NEC, or current 2020 NEC? There is some question as to which code will be applied to a very old, still open, city permit about to be inspected and closed.
These are located in a full kitchen. Code references would probably be helpful.