Just Mikey
Member
- Location
- Tennessee
- Occupation
- Electrical Contractor
Hello all, I've done accessory buildings with 60-100 amp panels in the past and the AHJ passed them without a hitch. I had one fail recently, and this is the first 8x10 accessory building I've done that I didn't put a panel inside. The homeowner just wanted a single 20 amp circuit for convenience outlets and a light. My service disconnect is a 20 amp rated switch where my conduit entered the building and the next device after my service disconnect switch is a 20 amp GFCI, then the light switch for the room lighting. Everything inside the shed is in pvc, because this is where the dogs stay to keep warm and I didn't want wiring to get chewed up and if their dogs are like mine, they will climb a wall to tear up whatever they can. So, there are no metal housings, all plastic. Anywho, I failed because I didn't install an electrode and a TR GFCI. The GFCI not being TR, I can get behind that was totally a slip on my part, but am I not meeting 250.32 (A)'s exception that doesn't require an electrode?
Anybody have anything similar to this? If the man wants an electrode, I'll give him one, but where am I going to land my electrode conductor?
Anybody have anything similar to this? If the man wants an electrode, I'll give him one, but where am I going to land my electrode conductor?