julian padilla
Member
- Location
- Houston, TX, USA
If the fryer has a nameplate rating of 20 A, what would be the maximum allowable standard rating of the fuse protecting the branch-circuit, 20 or 25 A? Any code references would be greatly appreciated!
Article 422 states 125% of the "continuous" load, and while the installation does not state this is a continuous load, my gut feel is that OCP should not be loaded to exceed 80 percent, so 20 x 1.25 = 25 A seems like the correct breaker size.
Please advise.
Julian
Article 422 states 125% of the "continuous" load, and while the installation does not state this is a continuous load, my gut feel is that OCP should not be loaded to exceed 80 percent, so 20 x 1.25 = 25 A seems like the correct breaker size.
Please advise.