Using the Point-to-Point calculation method, is there a method that would allow taking into account the X/R ratio.
Also, reading that if X/R is not provided from utility, acceptable to use value of 12 as basis of design. Agree or Disagree ?
There is a number of software programs out there that make use and allow you to accumulate the X/R ratio from point to point along the system route to the short circuit point. Look at SKM, EasyPower, CYME and others. If you are doing the calculations by hand, the impedance calculations you are coming up with gives you the X/R at any point of interest.
Also, every Utility I have worked with to date has given me the available fault current and X/R ratios for the three phase, and single phase faults at the point of contact (POC). If requested, I have also received the symmetrical components for impedance at the POC.
I hope I was able to answer your question since I may not understand just what you needed.