ACS580 using 4-20mA speed reference?

Learn the NEC with Mike Holt now!

Tip DS

I'm here.
Location
The Great Meme State
Occupation
Electrical Engineer
Being forced to abandon the ACS550, due to obsolescence. ABB says the ACS580 is the replacement. ACS550 accepted speed reference of 0-10V OR 4-20mA. The ACS550 dropped support for 4-20mA.

We have a DCS application, so voltage control is not a suitable option. Has anyone made this change? If so, what was your recipe? I'm not asking for theoretical approaches, I'm looking for successful implementations, including circuit details (such as resistor configuration) and parameter settings.

Thank you all.
 

4-20mA

an analog man in a digital world
Location
Charleston SC
Occupation
Instrumentation & Electrical
Can't you change the speed reference source to accommodate the mA input? AI1 can be told it's seeing V or mA I'm pretty sure, I know the 880's do. Maybe that will help
 

Tip DS

I'm here.
Location
The Great Meme State
Occupation
Electrical Engineer
Can't you change the speed reference source to accommodate the mA input? ...
Yes, as it turns out, the ACS580 still supports current as speed reference. I don't know why they changed the documentation, as it gives the appearance current speed control was dropped, but it wasn't. It does require the add-on daughter board, but doesn't require changing jumpers.

Thanks to @petersonra and @4-20mA for your input!
 
Top