ACSR FAULT CURRENT

Status
Not open for further replies.
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
POCO told me a couple days ago that if ACSR overhead cable is involved they give fault current calculations at the transformer secondary. Underground they will give to the meter. Reason being their calculator does not include an option for the ACSR. MHs calculator includes "Aluminum in Nonmetallic Raceway".

Is there a significant difference or close enough? The difference between AL in metallic vs non is a couple hundred amps for the single phase calcs I did to compare.
 
Overhead AL will have a higher reactance due to being spaced further apart. I'm surprised a POCO engineer hasn't been able to come up with an equation since ACSR spaced some level apart is universal for MV and HV.
 
I would think cable of any type would be spaced tighter than any three or four single conductors in any raceway.

You mean aerial bundled cable? In that case I'd think standard spacing in conduit would be a good enough estimate.

Though I am curious by how much twisting reduces X.
 