What is ACT cable, and what is it used for? For some reason I'm having a hard time finding it on Google... Thanks
III. Construction Specifications
320.100 Construction. Type AC cable shall have an armor
of flexible metal tape and shall have an internal bonding
strip of copper or aluminum in intimate contact with the
armor for its entire length.
320.104 Conductors. Insulated conductors shall be of a
type listed in Table 310.104(A) or those identified for use in
this cable. In addition, the conductors shall have an overall
moisture-resistant and fire-retardant fibrous covering. For
Type ACT, a moisture-resistant fibrous covering shall be
required only on the individual conductors.
Can you explain a bit more about where this question is coming from? Without knowing more, I'd guess that what you're looking at is referencing "Advanced Cable Ties" or the wire used to suspend drop ceilings.
:lol: Where have you ever seen AC cable with XHHW conductors?
No. Whoever wrote that question didn't have a clue. Read 320.104 again and think about how AC cable is constructed. There is your answer.
-Hal
The thermoset/thermoplastic issue is irrelevant to the user and is proprietary to the manufacturer of the cable. You would have to work for the cable manufacturer to know that since conductors are not marked.
-Hal
It's easy to tell thermoset from thermoplastic by heating it with a lighter.
What's a lighter?:angel: