I'm inspecting a job I did not design, so I'm already a lit confuzzled, and I could use some help.
It's a residence hall.
The "2 foot" NEC rule for counter top receptacles is in play.
However, it is an ADA unit.
I noticed the receptacles above the L-shaped counter were more than 48 inches apart.
When asked why there wasn't one closer to the corner, the electrician stated it wouldn't meet ADA; i.e., someone in a wheelchair couldn't reach the receptacle if it weren't directly in front of one of the front edges of the counter.
Can anyone confirm this, and perhaps lead me to the applicable code?
Ironically, if they had simply installed the receptacle closer to the corner, but still in front of the inside counter edge, they could still have met the NEC requirement, as the receptacle in question is probably only 10 inches from the stove counter cutout.
I don't want to be a jerk, but the code is what it is.