S shortcircuit1 Senior Member Location USA Oct 18, 2018 #1 Is there any mounting height requirement for load centers in ADA units?
rcarroll Senior Member Location Fort Collins, Colorado Oct 18, 2018 #2 There's some info in Annex J in the back of the NEC. The accessible units I inspect, the EC installs the outlets at 18" AFF & the panel top at 4'.
There's some info in Annex J in the back of the NEC. The accessible units I inspect, the EC installs the outlets at 18" AFF & the panel top at 4'.
S shortcircuit1 Senior Member Location USA Oct 18, 2018 #3 rcarroll said: There's some info in Annex J in the back of the NEC. The accessible units I inspect, the EC installs the outlets at 18" AFF & the panel top at 4'. Click to expand... I looked at the annex J i guess load centers fall under unobstructed reach froward so 48"max.
rcarroll said: There's some info in Annex J in the back of the NEC. The accessible units I inspect, the EC installs the outlets at 18" AFF & the panel top at 4'. Click to expand... I looked at the annex J i guess load centers fall under unobstructed reach froward so 48"max.