wondering what luck anyone has had with add-a-phase converters . there will be a 40hp 480v pump. static converter, roto phase, or digital. it is a rural area and the poco could not provide 3-phase to this sight. it is for a well pump.
 
We do maintenance on a motor generator 208 to 208/120 with 3 Phas-O-Matic (I think), they are rotary ten years and going strong.
 
I have read the static convertors don't last long and are dangerous. And they are meant for smaller hp motors. Never had any experiance with one.
 
Static converters have a place. . .they are the least expensive, initially.

I had one that I was called to troubleshoot. A 240V 3? roof top AC had lost a compressor, which had been replaced. Now, the new compressor just buzzed loudly, when energized.

The static converter "start" capacitor bank (about a dozen electrolytics, as I recall) were all blown. The "run" capacitor bank tested OK. I put in the new caps. . .and the compressor still buzzed.

After a period of self reflection, I crawled into and over the new compressor to read it's label. Lo and behold, the replacement was a 480 Volt unit! I locked out and tagged out the power, and left the news with the owner. Once the compressor was replaced again, the RTunit worked fine.

I guess my point is: The "3rd phase" is a capacitor shifted leg from the single phase. The timing of the 3 phases is not even which gives rise to additional vibration and energy loss. The motor will have a more stressed life. If the motor is automatically run, like my RTU example, loosing the start capacitors can leave the motor single phased.
 