Birken Vogt
Senior Member
- Location
- Grass Valley, Ca
I need to consult the poco on this, but wondering your thoughts or tell me to knock it off.
480 volts, 800 amps comes up from floor into interior wall mounted switchgear. Hits an 800 amp breaker, then bus bars over to a section with a bank of 6 or 9, 200 amp, direct reading meters.
Customer now controls all spaces so individual metering is not needed.
This job is to install a transfer switch that covers the entire building.
Is it possible or usual to install a CT metering setup over existing busbars like this? So we can transfer the whole load?
480 volts, 800 amps comes up from floor into interior wall mounted switchgear. Hits an 800 amp breaker, then bus bars over to a section with a bank of 6 or 9, 200 amp, direct reading meters.
Customer now controls all spaces so individual metering is not needed.
This job is to install a transfer switch that covers the entire building.
Is it possible or usual to install a CT metering setup over existing busbars like this? So we can transfer the whole load?