Add main breaker to older Cutler Hammer 'CH' loadcenter?

Merry Christmas

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Does anyone know if Cutler Hammer residential 'CH' panels from the 80's -90's era can generally be converted from main lug to main breaker like other brands?
I am able to find any info on this, I have 200A main lug one that needs a 200A breaker.
Its not a 70's era 'split buss'.
Thanks in advance.
 
I think many of those can have a backfed 125A in two corners where there is a hole for a hold down clamp. If you need 200A I don't think that is possible. The stab limit in those is usually 140A and I think that includes the adjacent stab.

CH didn't seem to make those quad breakers to put 150 or 200 amps across 4 stabs like some other vendors.
 
Your best bet might be to use the guts and front cover of a new main-breaker panel.
The box doesn't look tall enough for a main breaker. I bet if you compare the height of this loadcenter and a new loadcenter the new one will be at least 6" taller.
 
Yeah thanks everyone for the ideas. I am looking into Larrys idea and if there is not room I'll replace the panel.
 