Existing building with the service etc. all existing. Adding one new panel being fed from a breaker in another panel.
Would this separate raceway and GEC be required run back to service switchboard as shown in attached?
 

Attachments

  • Screenshot 2023-01-27 104523.jpg
    Screenshot 2023-01-27 104523.jpg
    239.6 KB · Views: 19
What do you mean shown with the feeder? It looks like a separate conduit with only a GEC from the panel to the service.
IF the new panel is being fed from the existing panel and they both in the same building you only need a properly sized feeder to the new panel with an EGC complying with 250.122, 250.118
No GEC is required.
(The #8 would be correct for an EGC on a 100 amp feeder but not required if the feeder raceway meets 250.118)
 
Everyone agrees the GEC is not required but it is permitted to run a GEC from the panel as shown in the drawing.
 