SSDriver
Senior Member
- Location
- California
- Occupation
- Electrician
I need to add a bypass to a pump that is currently running on a VFD in case the VFD needs repair. I was planning on using 3 contactors and had a few questions. It will also have an HOA switch (VFD - OFF - Bypass) run from a control transformer not in my diagram that would power the 3 contactors in this bypass cabinet. The RIGHT and LEFT contactor would get power with the switch in VFD mode and the Center contactor would get power with the switch in Bypass mode.
Questions
1. I'm assuming I would want to remove the OL Relay in the VFD?
2. If I remove the OL in the VFD I would run the NC contacts from the removed VFD OL relay and run it to a set of NC contacts mounted to the center contactor in my diagram. The NC contacts on my diagrams OL Relay would go to the center contactors coil. Is this correct?
3. I was planning on having a Mechanical interlock between the CENTER and Right contactor. I wasn't sure if I should or would need another mechanical interlock on the LEFT and CENTER. I was worried that having multiple mechanical interlocks could cause issues with them jamming up when the LEFT and Right contactors are closing at the same time.
4. Do I need to add an stop signal somewhere to stop the VFD run command in case someone shuts the pump down via the bypass cabinet instead of the drive by accident?
5. What am I missing?
Questions
1. I'm assuming I would want to remove the OL Relay in the VFD?
2. If I remove the OL in the VFD I would run the NC contacts from the removed VFD OL relay and run it to a set of NC contacts mounted to the center contactor in my diagram. The NC contacts on my diagrams OL Relay would go to the center contactors coil. Is this correct?
3. I was planning on having a Mechanical interlock between the CENTER and Right contactor. I wasn't sure if I should or would need another mechanical interlock on the LEFT and CENTER. I was worried that having multiple mechanical interlocks could cause issues with them jamming up when the LEFT and Right contactors are closing at the same time.
4. Do I need to add an stop signal somewhere to stop the VFD run command in case someone shuts the pump down via the bypass cabinet instead of the drive by accident?
5. What am I missing?