pipe_bender
Senior Member
- Location
- Boston
- Occupation
- Electrician
OK grouding guru's
I am working on a old building where the panels don't have equipment ground bars and there are several new circuits with green wire I grouped all these wires under a lug I tapped in the panel with a sheet metal screw. (sloppy I know but I was in a rush)
The inspector noted on rough inspection that I need to add a proper ground bar and noted a bunch of code sections well the note got lost.
The panel-board is no longer made and there is no UL-listed ground bar kit, so am I right that under 250.118 the feeder EMT is a equipment grounding conductor but the panel is not unless I have a UL listed kit for that panel?
I know the mfr provided ground bars have special holes and sometimes a slot.
To make matters worse the original installer used a big concentric K/O and might have broken a extra 'tab'.
My fix;
I have added a generic equipment ground bar to the panel, I tapped two 10/32 holes and removed the paint behind the ground bar as I think code requires this.
I happen to have a grounding 'wedge', like a bond bushing you can add under a locknut, I jumpered a #6 from this wedge to the equipment ground bar.
Will this meet code for an effective ground fault path?
Thanks
I am working on a old building where the panels don't have equipment ground bars and there are several new circuits with green wire I grouped all these wires under a lug I tapped in the panel with a sheet metal screw. (sloppy I know but I was in a rush)
The inspector noted on rough inspection that I need to add a proper ground bar and noted a bunch of code sections well the note got lost.
The panel-board is no longer made and there is no UL-listed ground bar kit, so am I right that under 250.118 the feeder EMT is a equipment grounding conductor but the panel is not unless I have a UL listed kit for that panel?
I know the mfr provided ground bars have special holes and sometimes a slot.
To make matters worse the original installer used a big concentric K/O and might have broken a extra 'tab'.
My fix;
I have added a generic equipment ground bar to the panel, I tapped two 10/32 holes and removed the paint behind the ground bar as I think code requires this.
I happen to have a grounding 'wedge', like a bond bushing you can add under a locknut, I jumpered a #6 from this wedge to the equipment ground bar.
Will this meet code for an effective ground fault path?
Thanks