Hello and thank you in advance for your input on this.
I'm looking at a single family residential 100A service, a Murray main panel, 1980's vintage. It's in a very old 1800's house and various circuits have been added over the years. The 20 circuit Murray panel has a 100A main breaker. There is an electric cooktop-40A breaker, wall oven-40A breaker, dryer-30A breaker, laundry-20A, gas furnace15A. Plus general lighting and kitchen small appliance circuits. There is a spare 30A 2pole breaker that used to go to a 2nd floor dryer that is abandoned.
The owner plans to add a heat pump for AC and heat, with a back up gas furnace. The heat pump specs are shown below. I was considering using the spare dryer circuit, changing the breaker to 30A HACR type, installing the #10awg copper circuit and outdoor disconnect. Once I received the specs,I noticed the L.R. AMPS at 72.2.
Could this trip the 100AMP main breaker in the event some other loads are on, such as wall oven, dryer, etc? Due to the cost of the HVAC work the owner would like to avoid upgrading the service to 200A at this time, but it is a future plan. I know that LRA is the start up current happening in fractions of a second, but I am leery about it happening when other loads are on.
I'm looking at a single family residential 100A service, a Murray main panel, 1980's vintage. It's in a very old 1800's house and various circuits have been added over the years. The 20 circuit Murray panel has a 100A main breaker. There is an electric cooktop-40A breaker, wall oven-40A breaker, dryer-30A breaker, laundry-20A, gas furnace15A. Plus general lighting and kitchen small appliance circuits. There is a spare 30A 2pole breaker that used to go to a 2nd floor dryer that is abandoned.
The owner plans to add a heat pump for AC and heat, with a back up gas furnace. The heat pump specs are shown below. I was considering using the spare dryer circuit, changing the breaker to 30A HACR type, installing the #10awg copper circuit and outdoor disconnect. Once I received the specs,I noticed the L.R. AMPS at 72.2.
Could this trip the 100AMP main breaker in the event some other loads are on, such as wall oven, dryer, etc? Due to the cost of the HVAC work the owner would like to avoid upgrading the service to 200A at this time, but it is a future plan. I know that LRA is the start up current happening in fractions of a second, but I am leery about it happening when other loads are on.