We are changing out our 12,470 volts to 480 volt delta delta transformer to a 480 volt Y transformer and our existing switchgear does not have a neutral bar. Is it up to code to add a neutral bar to the existing switchgear? I have attached a picture that shows the inside of the existing switchgear.
i ran into this with a new installation. gear was 3 wire, poco approved it, then said
i needed a 4 wire, as the neutral was needed for the new meter. no four wire loads.
had to add a neutral bus. gear manufacturer would not sell the factory parts.
would add them for five figures.
needed about 2' of bus bar. made it out of copper, put it in, poco would bless it
if city inspector blessed it?
city inspector blessed it.
so, to make it "up to code" you'd have to use factory furnished stuff, or have
them upgrade it.
or bend up some bus bar like i did.