Adding a Tesla charger onto an existing 150A service?
tx2step
I'm out of town without a code book, and one of my co workers sent the following load calc to me to check tonight!
He is wanting to add a Tesla car charger to an existing service without upsizing the existing 150A 120/240 service. I've never installed a Tesla charger - it'll be put on a 100/2 circuit breaker added to the existing panel. I think he left off the 120 V air handler for the a/c (I think he is only showing the condenser), plus I think the Tesla charger may run for over 3 hours and should be figured as a continuous load? Is that correct?
I can't reach him tonight to ask him any questions, and I'm going to be busy tomorrow!
Can any of you guys see anything missing or done incorrectly? I don't do many residential load calcs, and can't do a manual one in my head without a code book & appendixes to refer to (and my computer).
What do you guys think?
Thanks for the help!
Existing residence with a 150 amp 120/240 service
GENERAL LIGHTING LOADS:
1,922 sq. ft. x 3 va/sq. ft = ​5,766 va
2 sm. appl. circuits = ​3,000 va
1 laundry circuit = ​1,500 va
Total = ​10,266 va
First 3,000 @ 100% = ​3,000 va
7,266 va @ 35% = ​2,543 va
Total general lighting load = ​[5,545 va]
1 DRYER = ​[5,000 va]
(Range & water heater gas)
APPLIANCE LOADS:
1 microwave 120 v/15 amp​1,800 va
1 dishwasher 120 v/10 amp​1,200 va
1 disposal 120 v/6.5 amp​ 780 va​
1 Tesla car charger circuit
240 v/80 amp load​19,200 va
Total appliance load = ​22,980 va
22,980 va x 75% = ​[17,235 va]
HEATING & A/C LOADS:
1 central A/C unit
240 v/25 amp​[6,000 va]
(gas heat – omit)
25% largest motor (A/C)​[1,500 va]
TOTAL SERVICE LOAD = ​35,280 va / 240 volts = 147.0 amps
150 amp, 120/240 volt, single-phase service existing
tx2step
Does anyone know how long the charge time for a Tesla is? If it's 3 hours or more, that would shoot down his idea.
He wants to submit his calc to a plans examiner tomorrow, but I don't think it'll be approved!
ActionDave
Chief Moderator
Durango, CO, 10 h 20 min from the winged horses.
Licensed Electrician
Continuous load is one that pulls Maximum current for three hours. I would think the load on a battery charger would taper off.
tx2step
A Tesla is all electric. If it is close to fully discharged, I'm thinking it will be charging at 100% for quite a while so they can advertise as short an overnight or travel recharge time as possible. But I don't have any experience with them, so I don't really know. I was hoping someone here would know, since I'm sure that some on the forum have put several in by now.
Thanks!!!
GoldDigger
Placerville, CA, USA
Retired PV System Designer
The load on a battery charger for a lead acid battery will taper off once the State Of Charge (SOC) gets above about 80%.
But the Tesla battery is a high performance Lithium chemistry battery pack with cell level monitoring and cooling. The rapid charger would not have to taper off much if at all as it approached the 80-90% SOC that is probably the top of the normal operating range of such a battery pack.
The length of time depends on the charger speed and the size of the battery pack. The standard Tesla 240VAC charger draws 40A and can take 8 hours or more for a full charge on an 80kWH pack.
BTW, the Tesla Supercharger station uses a direct connection to the battery to do a 50-80% charge (depending on battery pack size) in under 1/2 hour. But that is not relevant to home charging.
tx2step
That is what I was thinking. It will probably charge at 100% for at least 3 hours...maybe longer. Also I didn't see the air handler blower motor in his service calc, and it'll be operating if the condenser is running.
His service calc is so marginal at 147A that I think the blower motor alone would push it over.
Looks like to me the service needs to be upgraded to a 200A?
ActionDave
Chief Moderator
:? $85? I think I missed something. I sounds like you are saying you pay about a buck per kWh.
You're off by a magnitude of order: more like $8.50-$10. or 40+MPG @ $2/gal gas prices.
Sitting on my couch running numbers through my head, 10 and .10 look a lot alike up there this time of night.
That's still quite a jump in my electric bill compared to gassing up my '98 Honda that will go 400 miles on twelve gallons of gas.
drcampbell
The Motor City, Michigan USA
Registered Professional Engineer
... That's still quite a jump in my electric bill compared to gassing up my '98 Honda that will go 400 miles on twelve gallons of gas.
$9 for a 200-mile fill-up vs. $30 for a 400-mile fill-up? Seems like a pretty good deal even if gasoline prices remain low, we never encounter another shortage and you don't install solar panels.