I'm out of town without a code book, and one of my co workers sent the following load calc to me to check tonight!
He is wanting to add a Tesla car charger to an existing service without upsizing the existing 150A 120/240 service. I've never installed a Tesla charger - it'll be put on a 100/2 circuit breaker added to the existing panel. I think he left off the 120 V air handler for the a/c (I think he is only showing the condenser), plus I think the Tesla charger may run for over 3 hours and should be figured as a continuous load? Is that correct?
I can't reach him tonight to ask him any questions, and I'm going to be busy tomorrow!
Can any of you guys see anything missing or done incorrectly? I don't do many residential load calcs, and can't do a manual one in my head without a code book & appendixes to refer to (and my computer).
What do you guys think?
Thanks for the help!
Existing residence with a 150 amp 120/240 service
GENERAL LIGHTING LOADS:
1,922 sq. ft. x 3 va/sq. ft = 5,766 va
2 sm. appl. circuits = 3,000 va
1 laundry circuit = 1,500 va
Total = 10,266 va
First 3,000 @ 100% = 3,000 va
7,266 va @ 35% = 2,543 va
=======
Total general lighting load = [5,545 va]
1 DRYER = [5,000 va]
(Range & water heater gas)
APPLIANCE LOADS:
1 microwave 120 v/15 amp1,800 va
1 dishwasher 120 v/10 amp1,200 va
1 disposal 120 v/6.5 amp 780 va
1 Tesla car charger circuit
240 v/80 amp load19,200 va
Total appliance load = 22,980 va
22,980 va x 75% = [17,235 va]
HEATING & A/C LOADS:
1 central A/C unit
240 v/25 amp[6,000 va]
(gas heat – omit)
25% largest motor (A/C)[1,500 va]
TOTAL SERVICE LOAD = 35,280 va / 240 volts = 147.0 amps
150 amp, 120/240 volt, single-phase service existing
He is wanting to add a Tesla car charger to an existing service without upsizing the existing 150A 120/240 service. I've never installed a Tesla charger - it'll be put on a 100/2 circuit breaker added to the existing panel. I think he left off the 120 V air handler for the a/c (I think he is only showing the condenser), plus I think the Tesla charger may run for over 3 hours and should be figured as a continuous load? Is that correct?
I can't reach him tonight to ask him any questions, and I'm going to be busy tomorrow!
Can any of you guys see anything missing or done incorrectly? I don't do many residential load calcs, and can't do a manual one in my head without a code book & appendixes to refer to (and my computer).
What do you guys think?
Thanks for the help!
Existing residence with a 150 amp 120/240 service
GENERAL LIGHTING LOADS:
1,922 sq. ft. x 3 va/sq. ft = 5,766 va
2 sm. appl. circuits = 3,000 va
1 laundry circuit = 1,500 va
Total = 10,266 va
First 3,000 @ 100% = 3,000 va
7,266 va @ 35% = 2,543 va
=======
Total general lighting load = [5,545 va]
1 DRYER = [5,000 va]
(Range & water heater gas)
APPLIANCE LOADS:
1 microwave 120 v/15 amp1,800 va
1 dishwasher 120 v/10 amp1,200 va
1 disposal 120 v/6.5 amp 780 va
1 Tesla car charger circuit
240 v/80 amp load19,200 va
Total appliance load = 22,980 va
22,980 va x 75% = [17,235 va]
HEATING & A/C LOADS:
1 central A/C unit
240 v/25 amp[6,000 va]
(gas heat – omit)
25% largest motor (A/C)[1,500 va]
TOTAL SERVICE LOAD = 35,280 va / 240 volts = 147.0 amps
150 amp, 120/240 volt, single-phase service existing