My question is ,
I need to add load to a 45kva transformer and I am wondering if it will handle the additional load.
480v bus duct feeds transformer
Delta to wye transformer
120/208 out put
100 amp primary fused
3 phase
So I primary = 45000va / (480v x 1.732) = 54 amp primary
I secondary = 45000va / (208v x 1.732) = 125 amp secondary .
So does that mean I have 125 amps on phase A,B&C . Or 125amps split between the 3 phases.
120 Power is supplied once every three floors via a 45kva transformer and 100 amp disconnect off the 480v bus duct.
The load that I am adding is one 20 amp circuit per room per floor of hotel. So worst case scenario 16 amp x 120v =1920w , 1920w x 16 rooms per floor =30,720w , 30,720w x 3 floors = 92,160w . This is assuming everyone would be using the extra load to its full potential all at the same time .
What I am asking is if I add 3 subpanels to bring 120v power to each floor, 100 amp panels 3 phase , all running off existing 120v 3 phase 125amp panel fed by the 45kva transformer , would I be overloading the existing installation.
Any help would be greatly appreciated .
I need to add load to a 45kva transformer and I am wondering if it will handle the additional load.
480v bus duct feeds transformer
Delta to wye transformer
120/208 out put
100 amp primary fused
3 phase
So I primary = 45000va / (480v x 1.732) = 54 amp primary
I secondary = 45000va / (208v x 1.732) = 125 amp secondary .
So does that mean I have 125 amps on phase A,B&C . Or 125amps split between the 3 phases.
120 Power is supplied once every three floors via a 45kva transformer and 100 amp disconnect off the 480v bus duct.
The load that I am adding is one 20 amp circuit per room per floor of hotel. So worst case scenario 16 amp x 120v =1920w , 1920w x 16 rooms per floor =30,720w , 30,720w x 3 floors = 92,160w . This is assuming everyone would be using the extra load to its full potential all at the same time .
What I am asking is if I add 3 subpanels to bring 120v power to each floor, 100 amp panels 3 phase , all running off existing 120v 3 phase 125amp panel fed by the 45kva transformer , would I be overloading the existing installation.
Any help would be greatly appreciated .