Adding an external ground to 2" LFMC

Carl24x

Member
Location
Decatur MS
Occupation
Electrical Mgr
Looking to see what could be used to install an external ground on the outside of a piece of 2" LFMC in a class 1 Div 2 area. My flexible connectors do not have provisions to install a ground on them and are too thin to tap. It's been a while but i recall using something split that you could loosen the nut, install and retighten connector providing a means to install a ground. I wanted to see if anyone recalled the part i'm looking for while i continue to look.

Thanks,
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Thomas & Betts makes a LTM connector with a ground lug, and a ring that camps over the fitting to take an EGC, I used to stock all the sizes of the rings.
They would be special order but a distributor like Graybar may have in their system
 

Carl24x

Member
Location
Decatur MS
Occupation
Electrical Mgr
I was able to find a T & B grounding strap that fits over a their connector but it only goes to 1 1/4". we were able to tap it out and install a machined screw. Looks like an after thought but it's better than a tek screw.

Thank you
 