There is an existing installation to which the customer wants to add two new circuits. The existing installation has a trough with key taps feeding four (4) 200 AMP disconnects. 120/208 3 ph. the trough is 12" x 12" x 60"(LENGTH). The existing cable in the trough is 4#3/0 for each 200 amp breaker (total 16 3/0) and 2 sets of 500 MCM feeders from the transformer (total 8 500MCM). New cable to be added to the tough is to be 4 #4 feeding a new 80 amp disconnect and 4 350 MCM feeding a new 300 amp disconnect. These new cables will be terminated on the key taps in the trough. Is the trough size acceptable per NEC? Can the existing feeders (2 sets 500MCM per phase) carry the additional load being added?