Conductor derating is probably not a problem if you are working with THHN in sizes 10, 12, and 14 AWG.
You can put as many as 9 current carrying conductors in a raceway/conduit with 70% of the 90 degree rating. The 90 degree rating for THHN in 14, 12, and 10 AWG per Table 310.16 is 25, 30, and 40 Amps; so 70% is 17.5, 21, and 28 Amps. Those values exceed the maximum OCPD for the 14 and 12, and you are permitted by NEC 240.6 to use a 30 Amp breaker with the #10 for the 28 Amp ampacity.