Adding air conditioning to a building that has a service sized for electric heat but no spare.
Noncoincident:
1. Cooling and heating noncoincident enough and no further action (control) required?
2. The electric heat serves a different area for than the cooling. If the cooling is heat pumps which could be coincident, can we add control so one is disabled if the other is in use?
In this case it could be done in the control circuit of the heating – or – could be done but disabling the power to the heating (shunt trip breaker or something).
Bonus question:
Does not apply in this case but – 220.51 - Does a 2 stage electric heat coil in an air handling unit count as “fixed electric space heating”?
Noncoincident:
1. Cooling and heating noncoincident enough and no further action (control) required?
2. The electric heat serves a different area for than the cooling. If the cooling is heat pumps which could be coincident, can we add control so one is disabled if the other is in use?
In this case it could be done in the control circuit of the heating – or – could be done but disabling the power to the heating (shunt trip breaker or something).
Bonus question:
Does not apply in this case but – 220.51 - Does a 2 stage electric heat coil in an air handling unit count as “fixed electric space heating”?