(Add) 9.6.9.8
The color code for all newly installed fire alarm system conductors shall be as follows:
(1) INITIATING DEVICE CIRCUIT shall be red and black. Red shall be positive and black shall be negative [IDC/SLC].
(2) NOTIFICATION APPLIANCE CIRCUIT shall be blue and white. Blue shall be positive and white shall be negative. When speakers, bells, chimes or other audible/visual devices are used in lieu of horns, this color code shall be followed [NAC].
(3) STROBE CIRCUIT, if a separate feed is required, shall be blue and white. Blue shall be positive and white shall be negative.
(4) SMOKE DETECTOR CIRCUITS, if a separate power feed is required, shall be brown and violet. Violet shall be positive and brown shall be negative.
(5) “LOCAL” SMOKE DETECTOR CIRCUITS, if an interconnect wire between sounder bases is required, shall be violet.
(6) AUXILIARY REMOTE POWER SUPPLY CIRCUITS shall be brown and violet.
Violet shall be positive and brown shall be negative.
(7) ELECTRO-MAGNETIC DOOR HOLDBACK CIRCUITS shall be gray and gray if powered by 24 vDC or black and white if powered by 120 vAC.
(8) MUNICIPAL MASTER BOX TRIPPING CIRCUITS shall be orange and orange.
Conductors for this circuit shall be installed in a separate raceway. (9) ELEVATOR CAPTURE CIRCUITS shall be brown and yellow.
(10) HVAC SHUTDOWN CIRCUITS and AUDIO/VISUAL SYSTEMS SHUTDOWN CIRCUITS shall be orange and yellow.
(11) REMOTE ANNUNCIATOR CIRCUITS shall be violet and numbered at each end or as required by the control unit manufacturer.
(12) MUNICIPAL FIRE ALARM LOOP from the master box to the municipal loop shall be black and white.