Marty Lustig
Member
- Location
- Prairie Village, KS
I'm relatively new to the Forum, so if this topic has been covered in depth previously, just point me in the right direction, please. I'm working in an older home (1950's) wired with Romex (2 wire without ground) for much of it. Where a true equipment ground is not required, I've put in GFCIs (combined with AFCI's in most places). However, there are some places where having an equipment ground would be very desirable...various electronic equipment. I'm looking for some "best" (or at least "good") practices for running an equipment ground back to panel. Getting TO the panel from most of the critical need locations would (naturally) be extremely difficult. I CAN get to the #4 running from panel to cold water pipe into house quite easily. Questions: 1. Can I run a grounding green #12 from JBox through same opening/clamp as Romex is going, wire tie the grounding wire to the Romex for as much as I can, then "branch" over to the #4 and connect with a split-bolt approved for the #4. 2. What about locations that are not near anything that is grounded. Does anyone run a grounding wire outside the house and eventually to the panel or to the #4 running to water pipe?