adding lights to a service entrance/metering pole

Status
Not open for further replies.

fackerman1

New member
I have an outdoor location and a 25' pole with a service entrance feed (fed from a 25kva transformer on another pole 20' away) down to a meter and a 200a disconnect switch. This equipment is located on the front of the pole at 15' and below. Is there any reason I could not run a 1" conduit up the back of the pole and add 2 flood lights on adapters at a heigth of 19', 4' above my goose neck service feed?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

Provided that there is proper overcurrent protection for the lighting circuit there is nothing in the NEC that would prohibit you running back up a pole that has a service mast to feed lights.

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You might consider ownership of the pole. If owned by the utility, they often have a say as to what is attached to their poles.
 

stevebea

Senior Member
Location
Southeastern PA
I have an outdoor location and a 25' pole with a service entrance feed (fed from a 25kva transformer on another pole 20' away) down to a meter and a 200a disconnect switch. This equipment is located on the front of the pole at 15' and below. Is there any reason I could not run a 1" conduit up the back of the pole and add 2 flood lights on adapters at a heigth of 19', 4' above my goose neck service feed?

Wouldn't this have to be a customer owned pole? I can't believe POCO would let service equipment be mounted on their pole.
 