Hi There! My company is working on an electrification project at 12 unit apartment building. We hired an MEP to determine if the existing 200A service, which serves both the house meter and all (12) 60A apartment panels, has sufficient capacity to handle the new load. However, I am concerned that the electrical engineer is not familiar with the appropriate methodology or calculations, so I decided to turn to this community to get a second opinion.
We are planning to install a ducted mini split in each apartment (NTXDKS18A112A & NTXSKS18A112A) to replace the existing fan coil (~ 3 amps). The fan coils are supplied with heated and chilled water that comes from a central plant that is on a completely different electrical service. We are also planning to install a central heat pump hot water heater to serve all 12 units. Once again, domestic hot water was previously supplied by a central plant. We performed a load study of the existing 200A service and measured the peak demand over a 7 day period. According to the electrical engineer, the max load was 25.12 kW, or 87.26 A.
My first, and primary question, is likely a simple one. When calculating the added load of the new equipment, what number should we be using from the attached spec sheets? My understanding is that he should use the MCA, but he is using a value that is a good deal below MCA. Thanks in advance for your help!
We are planning to install a ducted mini split in each apartment (NTXDKS18A112A & NTXSKS18A112A) to replace the existing fan coil (~ 3 amps). The fan coils are supplied with heated and chilled water that comes from a central plant that is on a completely different electrical service. We are also planning to install a central heat pump hot water heater to serve all 12 units. Once again, domestic hot water was previously supplied by a central plant. We performed a load study of the existing 200A service and measured the peak demand over a 7 day period. According to the electrical engineer, the max load was 25.12 kW, or 87.26 A.
My first, and primary question, is likely a simple one. When calculating the added load of the new equipment, what number should we be using from the attached spec sheets? My understanding is that he should use the MCA, but he is using a value that is a good deal below MCA. Thanks in advance for your help!