Hypothetical Situation
Say you have a building with a 200A, 208V, 3Ph service.
And say the highest demand in the last 12 months per the utility is 80A.
So based on 220.87 you have 100A available for added loads.
However – the building has an infrequently used elevator. (95FLA, 195A start, 65.1A rated)
Say the building has three 5 ton 1 phase air conditioners (and maybe 6000W lighting).
Do you think the elevator shows up in the demand?
Bottom line - would you account for the elevator on top of the demand?