I am being asked to quote a design to add a generator that would back up a full 6 unit condo with house power (includes elevator) that was built in the 70's. Besides knowing that cost will be too much, I see a fire pump issue that I am wondering if anyone sees a solution too. A utility transformer feeds 3 phase power into a 1200A MLO ITE panelboard. an 800A breaker send a feed to a meter center (not a problem). a 300A breaker feeds a small wireway with 2 taps (1 to an elevator fused disconnect) and the other a 225A MB panel (House Panel). ONe of the house panel circuits has a 3 pole 60A breaker that goes to a fire pump room's (through the building) controller.
Today I would assume you would require a generator as I am sure the power source isn't reliable. I would also supply the service to the UL listed controller from a source before the 1200A panelboard.
That being said, is it worth even thinking I might be able to just install a generator to an ATS that feeds the 1200A panelboard and just ignore what is a downstream problem? Or should I assume we will need to pull the fire pump controller off the house panel? The existing controller doesn't even have a breaker in it so that would then have to be upgraded to a service rated UL controller. If I replace that then I worry they will say I now have to supply a generator to it. Just trying to figure out how address this in my proposal. Further the feed to the existing 1200A panelboard comes up from the bottom and just to tap ahead of that panelboard will require a separate run from the transformer to be ran.
Today I would assume you would require a generator as I am sure the power source isn't reliable. I would also supply the service to the UL listed controller from a source before the 1200A panelboard.
That being said, is it worth even thinking I might be able to just install a generator to an ATS that feeds the 1200A panelboard and just ignore what is a downstream problem? Or should I assume we will need to pull the fire pump controller off the house panel? The existing controller doesn't even have a breaker in it so that would then have to be upgraded to a service rated UL controller. If I replace that then I worry they will say I now have to supply a generator to it. Just trying to figure out how address this in my proposal. Further the feed to the existing 1200A panelboard comes up from the bottom and just to tap ahead of that panelboard will require a separate run from the transformer to be ran.