I have a job coming up ( 2020 NEC) which requires us to add a breaker in a main lug 125 amp panel being used as service equipment.
Aka 6 handle rule.
The panel is 12/24 which would allow more the 6 two pole breakers.
The new service disc would be for a room addition feeder.(60 amp).
The existing meter will be changed from 100 to 200.
Which has a double lugged load side.
By adding this main would it be a violation of service mains in the same enclosure?
FYI, the other double lugged service conductors run inside to a main breaker panel.
I see that as an issue as well
Right now the outside existing main lug has two AC units and back feed PV in it.
I see the PV as a line side tap.
Which is feed from a PV system on a detached structure( garage) with a separate service.
There adamant this is ok to do.
Aka 6 handle rule.
The panel is 12/24 which would allow more the 6 two pole breakers.
The new service disc would be for a room addition feeder.(60 amp).
The existing meter will be changed from 100 to 200.
Which has a double lugged load side.
By adding this main would it be a violation of service mains in the same enclosure?
FYI, the other double lugged service conductors run inside to a main breaker panel.
I see that as an issue as well
Right now the outside existing main lug has two AC units and back feed PV in it.
I see the PV as a line side tap.
Which is feed from a PV system on a detached structure( garage) with a separate service.
There adamant this is ok to do.