Looking at wiring a detached garage approximately 260 feet from house. There's not much in the garage, I believe about 6 or 8 receptacles and 2 garage door openers and some LED lights. A 10/3 uf would probably surfice but with the price of copper these days, decided to go with #2 AL 4 conductors.
Was going to install a 100 amp sub-panel In the garage. Can the #2 AL be on a 100 amp breaker if the load is way under 90 amps? Load will probably never see 20 amps.
Also he is planning on installing, I believe 5 kw of solar at the garage to back-feed to the house. That's another reason for the upsize of the wire feeding from the house to the garage. The house has a 400 amp meterbase with 2-200 amp panels in the basement. The solar company told me all they needed was a 100 amp disconnect at the garage for them to attach their wires to. Does this sound correct and does the 2 AL work for this application?
Was going to install a 100 amp sub-panel In the garage. Can the #2 AL be on a 100 amp breaker if the load is way under 90 amps? Load will probably never see 20 amps.
Also he is planning on installing, I believe 5 kw of solar at the garage to back-feed to the house. That's another reason for the upsize of the wire feeding from the house to the garage. The house has a 400 amp meterbase with 2-200 amp panels in the basement. The solar company told me all they needed was a 100 amp disconnect at the garage for them to attach their wires to. Does this sound correct and does the 2 AL work for this application?