I have been asked to give an estimate to a private school installing 4 -20 amp circuits for laser printers, and computers the Students learn on.
the building was built in the 1950s.
The electrical panel feeding the computer lab and existing fluorescent lights etc is a QOC30 (30) space MLO single pahse panel.
the neutral buss is totally filled with no room to add any more Nutral conductors. the feeders to this panel are cloth coverd Copper tinned ? conductors 2/0 or 4/0 can not find marking for wire size. panel is protected by a 200amp Fuse-able disconnect with 200A fuse's.
the Nutreal. and ground are tied together in the existing panel.
I would like to install a 60 Amp subb panel next to the existing panel and relocate 2- 20 amp existing circuits to sub panel to make room for the 60A sub main.
if I separate the ground and neutral and the Sub I should be OK.
what if any could be issues with this.
the job will be inspected by the AHJ since this is for a School.
I do not know what the fault current rating is on this panel or main service. main service comes in to a gutter and then tapps off to feed several 200A disconects to other panels the Building
the building was built in the 1950s.
The electrical panel feeding the computer lab and existing fluorescent lights etc is a QOC30 (30) space MLO single pahse panel.
the neutral buss is totally filled with no room to add any more Nutral conductors. the feeders to this panel are cloth coverd Copper tinned ? conductors 2/0 or 4/0 can not find marking for wire size. panel is protected by a 200amp Fuse-able disconnect with 200A fuse's.
the Nutreal. and ground are tied together in the existing panel.
I would like to install a 60 Amp subb panel next to the existing panel and relocate 2- 20 amp existing circuits to sub panel to make room for the 60A sub main.
if I separate the ground and neutral and the Sub I should be OK.
what if any could be issues with this.
the job will be inspected by the AHJ since this is for a School.
I do not know what the fault current rating is on this panel or main service. main service comes in to a gutter and then tapps off to feed several 200A disconects to other panels the Building