addition of neutral to existing feeders to existing three-phase panel

Status
Not open for further replies.
I have an installation scenario where I am to provide a quotation to install one (1) 500KCMIL THHN conductor for a "neutral" to just one (1) set of three (3) sets of (3) 500KCMIL THHN current carrying conductors that originate from a central distribution switchboard and route and supply power to a distribution panelboard. From this distribution panelboard, we are to install and route in an existing raceway a neutral for a panelboard (this panelboard has just a single set of feeders).
My concern per section 310.4 of the electrical code (2011) is that the distribution panelboard with three (3) sets of feeders should have a neutral conductor in each of sets.
I have consulted with (2) engineers and (1) electrical inspector to seek their interpretation. The customer asks that I fullfil this request and deems one neutral in the distribution panelboard sufficient and will take care of the three-phase/neutral needs of the single set panelboard being supplied with power.
Any thoughts from my fellow electrics out there in weighing in on this? Am I missing something in this request? I have not received the inspection/engineering feedback as of this writing.
Thank you all
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If I'm reading the question correctly you are correct that you would need a neutral conductor in each of the parallel raceways. If one 500kcmil conductor is large enough for the calculated load then you might be able to get away with a #1/0 in each of the three raceways.

Welcome to the Forum. :)
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I'm not sure I understand correctly, but if the parallel's are all in 1 conduit you could have just 1 neutral (assuming the load calc supports it).
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I'm not sure I understand correctly, but if the parallel's are all in 1 conduit you could have just 1 neutral (assuming the load calc supports it).
I would really doubt that there are three sets of 500's in a single conduit.
 