Addition to Existing Building - Service is in Existing Building - Is a UFER required for the addition?

Jonny Quest

New User
Location
Illinois
Occupation
Plan Reviewer
An addition is proposed to an existing building, and the existing service is in the existing building. Are we still required to provide a concrete-encased electrode in the footing of the new addition? If so, how is the UFER connected to the existing service?

Thanks

JQ
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Since this is an addition any new electrode would need to be tied to the existing building GES. A CEE is only require where there is 20' or more of 1/2" or larger rebar in the footing in contact with the earth. If there is an existing CEE for the existing building another one for the addition is not required.
 