cvanhouten
Member
I have a situation were our Standby Generator is located 53 feet from the building. We are using a 3-pole transfer switch and have a solid neutral through the transfer switch. Thus, we do not have a separately derived system correct. In the code book it say if the generator is within sight of the building than you do not need an additional disconnect means at the building. The definition of within sight say no more than 50 ft away. It also say if the conductors are not grounded. Wouldn't these conductors be grounded so we would not have to provide the extra disconnect? This is not a required emergency back by code, the owner has elected to provide a generator to backup the whole building (telephone co.) So the main service is 600A at 120/208V 3-phase. The transfer switch is in the building and service rated with the utility main breaker in the panel, the generator has a main breaker outside in the generator enclosure. Let me know if this is not enough information.
Thanks