I'm looking at a one-line diagram. The engineer shows the main cabinet outside the building with the first point of disconnecting means in "CTE" cabinet. He shows the neutral ground bond at this location and all the grounding electrode conductors connected to the buss. From here we feed through two 4pole automatic transfer switches to the first piece of gear on the load side of each transfer switch MSH and EHA. He shows additional set of grounding electrode connections to the buss in MSH, but the ground to neutral bond is not shown so thats all good. But, off the ground bus in this gear is a line noted "Equipment grounding conductor to ground bus in CTE sized per NEC 250.122. Do not bond neutral and ground busses in MSH or EHA". We already have ground conductors ran along with the feeders through the ATS to the equipment. What would be the reason for this additional noted ground, is it required by NEC?