No issue that I can see. 4-90's with 25% fill should go rather nicely.
But XHHW is the only insulation I spec for underground runs....lasts a lot longer than THWN. You do have to be careful with the fill on the smaller sized conductors as the OD for XHHW is bigger.XHHW insulation has more friction than nylon jacketed THHN. Bring some goop just in case.
Sent from my SM-A326U using Tapatalk
If aluminum, often is compact conductor and sort of evens things out to an extent again.But XHHW is the only insulation I spec for underground runs....lasts a lot longer than THWN. You do have to be careful with the fill on the smaller sized conductors as the OD for XHHW is bigger.
I've found XHHW usually seems to pull easier if it is cold outside.XHHW insulation has more friction than nylon jacketed THHN. Bring some goop just in case.
I totally agree. It gets really rubbery in the sun. Lol.I've found XHHW usually seems to pull easier if it is cold outside.
Having it laying in the sun before pulling on a hot day seems to pull the hardest.
Haven't really proven this in any way, but seems to be the way it is, when comparing similar pulling jobs but in different temp conditions.