I'm reading through section 500.5 (B) (2) (3): Class I, Division 2. A Class I, Division 2 location is a location:
"That is adjacent to a Class I, Division 1 location, and to which ignitable concentrations of flammable gases, flammable liquid–produced vapors, or combustible liquid– produced vapors above their flash points might occasionally be communicated unless such communication is prevented by adequate positive-pressure ventilation from a source of clean air and effective safeguards against ventilation failure are provided."
My questions are:
1. Does any unclassified space adjacent with door opening to Class 1 Div 1 makes it Class 1 Div 2?
2. If the classified spaces has an adequate positive pressure that will not classify the adjacent space, correct?
3. Not sure I understand "....effective safeguards against ventilation failure are provided", can you please explain how this could be accomplished?
4. Does conduit penetration between C1D1 and unclassified spaces makes the unclassified space C1D2? My thinking if we provided a seal around the conduit in the wall and conduit seals as required that should not classified the space, correct?
Thanks,
"That is adjacent to a Class I, Division 1 location, and to which ignitable concentrations of flammable gases, flammable liquid–produced vapors, or combustible liquid– produced vapors above their flash points might occasionally be communicated unless such communication is prevented by adequate positive-pressure ventilation from a source of clean air and effective safeguards against ventilation failure are provided."
My questions are:
1. Does any unclassified space adjacent with door opening to Class 1 Div 1 makes it Class 1 Div 2?
2. If the classified spaces has an adequate positive pressure that will not classify the adjacent space, correct?
3. Not sure I understand "....effective safeguards against ventilation failure are provided", can you please explain how this could be accomplished?
4. Does conduit penetration between C1D1 and unclassified spaces makes the unclassified space C1D2? My thinking if we provided a seal around the conduit in the wall and conduit seals as required that should not classified the space, correct?
Thanks,