Can someone please educate me on a question that I have. There is an existing Distribution Panel that is rated at 400A, 480V, 3 phase, 3 wire with 400A main breaker. I wanted to re-route an existing feeder from another existing Distribution Panel located in the same room to connect to the 400A, 480V, 3 phase, 3 wire Distribution Panel. My question is that the existing Distribution Panel that I want to re-route the feeder to the 400A distribution panel has a 600A adjustable trip main breaker. I checked and the main breaker can be set at 400A. My question is if the main breaker is rated at 600A and I can adjust the trip at 400A, is it allowable to connect to the 400A, 480V, 3 phase, 3 wire Distribution Panel since the Distribution Panel that I want to connect to has a 400A main breaker?
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
So you want to know if you can put an adjusted 400A breaker ahead of a fixed 400A breaker? Is the adjusted 400A breaker feeding any other circuits?
 

j2020

Member
Location
California
Occupation
Engineer
Yes. But the adjustable trip breaker is rated at 600A but can be adjusted down to 400A. The breaker is a main on a distribution panel that feeds mechanical equipment. My question is since the adjustable trip breaker is rated at 600A, if I adjust it down to 400A and connect it to a distribution panel with a fixed 400A breaker ahead of this distribution panel, is that allowable?
 

j2020

Member
Location
California
Occupation
Engineer
I have another question. If I tap the buss on the existing distribution panel and provide a feeder to the other distribution panel, can I just connect to the main breaker at the other distribution panel instead of providing an enclosed breaker next to the buss that I am tapping? The two distribution panels are next to each other. Maybe a little more than 10 feet apart. There is no physical space to provide a 400A breaker in the existing Distribution Panel.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have another question. If I tap the buss on the existing distribution panel and provide a feeder to the other distribution panel, can I just connect to the main breaker at the other distribution panel instead of providing an enclosed breaker next to the buss that I am tapping? The two distribution panels are next to each other. Maybe a little more than 10 feet apart. There is no physical space to provide a 400A breaker in the existing Distribution Panel.
As Rock stated you'll to know the maximum conductor length and then apply the appropriate tap rule in 240.21. Since you mentioned more than 10' it sounds like you'll need to apply the 25' tap rule.
 