drktmplr12
Senior Member
- Location
- South Florida
- Occupation
- Electrical Engineer
Industrial site, locked electric room
800A frame switchgear breaker with 400 amp trip unit. we want to connect #4/0 and adjust the trip down to 250. I see 240.4.C allows adjustment below maximum long time pickup only with restricted access. I am being told that if we adjust down from 1.0, the breaker needs to be labeled that the conductors are not rated for the full capacity of the trip unit. Haven't heard of this before and can't find a code reference.
Has anyone experienced a similar requirement from AHJ or has a code reference to help?
Thanks
800A frame switchgear breaker with 400 amp trip unit. we want to connect #4/0 and adjust the trip down to 250. I see 240.4.C allows adjustment below maximum long time pickup only with restricted access. I am being told that if we adjust down from 1.0, the breaker needs to be labeled that the conductors are not rated for the full capacity of the trip unit. Haven't heard of this before and can't find a code reference.
Has anyone experienced a similar requirement from AHJ or has a code reference to help?