pdr
Member
Annex B,Table B.310.11 "Adjustment Factors for More Than Three Current-Carrying Conductors in a Raceway or Cable with Load Diversity"
10-24 conductors........70% adjustment*
*These factors include the effects of a load diversity of 50 percent.
The calculation examples shown do not define if the 14 AWG THHN are being installed with existing 14 AWG THHN's.
Questions are;
1. Define "load diversity". (not in the definitions).
2. Clarify if the calculation can be used with conductors of the same insulation type, but with different size conductors.
Note; Table 310.15(B)(2)(a)
10-20 conductors........50% adjustment
10-24 conductors........70% adjustment*
*These factors include the effects of a load diversity of 50 percent.
The calculation examples shown do not define if the 14 AWG THHN are being installed with existing 14 AWG THHN's.
Questions are;
1. Define "load diversity". (not in the definitions).
2. Clarify if the calculation can be used with conductors of the same insulation type, but with different size conductors.
Note; Table 310.15(B)(2)(a)
10-20 conductors........50% adjustment