hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have #10awg 90C cable temp but terminals are rated at 60C.
Breaker feeding the cables is 30A. The cables in conduit have more than 4 current carrying conductors.
I have plans which state that at 90C its 40A and 40x0.8=32A. This is acceptable
However as I read 310.15(B) i think its incorrect because corrected ampacity 32A is greater than ampacity of 60C temp rating termination which is 30A.
So am I correct or incorrect in this case temperature rating of the conductor cannot be used and they need to increase the size?
Breaker feeding the cables is 30A. The cables in conduit have more than 4 current carrying conductors.
I have plans which state that at 90C its 40A and 40x0.8=32A. This is acceptable
However as I read 310.15(B) i think its incorrect because corrected ampacity 32A is greater than ampacity of 60C temp rating termination which is 30A.
So am I correct or incorrect in this case temperature rating of the conductor cannot be used and they need to increase the size?