when adjustment factors are used do you use the temp that the wire is rated for or do you use the temp that the terminals require?
EX. There are 6 #8 thhn current carrying conductors in a conduit, the terminals are rated at 60'c. Do derate at the 60'c or the 90'c column in 310-16.
EX. There are 6 #8 thhn current carrying conductors in a conduit, the terminals are rated at 60'c. Do derate at the 60'c or the 90'c column in 310-16.