Would anyone happen to know if load calculations for motors on Washington state administrator exam are based on nominal voltages 120/240 480 or are they based on 115/230 460 as listed in tables in code book. just doing a practice question with a 3/4 hp pool pump and 5 hp AC unit it means the difference between a 110a service and a 125a service and I have noticed it being done both ways in practice questions.
And yes using Mike Holt exam prep book
Thanks any help would be greatly appreciated

Tony S.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The code states:
220.5 Calculations.
(A) Voltages. Unless other voltages are specified, for purposes
of calculating branch-circuit and feeder loads, nominal
system voltages of 120, 120/240, 208Y/120, 240, 347,
480Y/277, 480, 600Y/347, and 600 volts shall be used.
I don't see any other requirement in 430.
 
Administrator test

Administrator test

Yes took test today and they call out voltage on questions and they are using nominal. On majority of questions I could not get exact number as far as volt amp or total amperage, I think it is a matter of interpretation, like weather sign power 1200va is considered continues or not and so on.
I just want to say thank you Mike Holt and staff your book Electrical exam preparation is the best money I have spent in this whole proses.

Look out Washington there is another Administrator in the house.