I know we cannot install a duplex receptacle face up in a countertop but adorne makes these receptacles that pop out. Why wouldn't that be compliant in a kitchen countertop?

white-pop-out-web.ashx


Here is a vid

 
There are several receptacle outlet assemblies listed for countertop applications that can be installed in compliance with 210.52(C) and 210.52(D). Most employ a "pop-up" type assembly in a fixed housing that is hard-wired into ne of the small-appliance branch-circuits. These products have special features that protect against liquids and other countertop hazards.
 
There are several receptacle outlet assemblies listed for countertop applications that can be installed in compliance with 210.52(C) and 210.52(D). Most employ a "pop-up" type assembly in a fixed housing that is hard-wired into ne of the small-appliance branch-circuits. These products have special features that protect against liquids and other countertop hazards.


Thanks. All the ones I have seen were god awful ugly. The old Mockett style was the best I have seen. I called Mockett and they said they have a TR and GFCI direct wired unit that has been at UL for 6 months. No telling when it will be available.

Here is the style we like but not sure this will be available anymore-- this one is cord and plug and I believe is not made anymore

PCS34-90-94-thumbnail.jpg
 
We have a 25 foot long continuous counter. The home owner wants to build a temp. box and install the receptacles and then remove them after inspection. I told them I would not be a part of that. They actually don't want and receptacles on the entire run.....:happyno:
 
We have a 25 foot long continuous counter. The home owner wants to build a temp. box and install the receptacles and then remove them after inspection. I told them I would not be a part of that. They actually don't want and receptacles on the entire run.....:happyno:

Have you thought about Plugmold on the underside of the countertop?
 
Have you thought about Plugmold on the underside of the countertop?


Bite your tongue.... :D We have offered everything available . Apparently the uppers are 21" high so it would not be compliant. I could get the inspector - perhaps- to agree but then the issue is the is not a front style(sp) around the cabinet to recess it in. We even talked about recessing the plugmold to no avail. They will have to decide on something soon
 