I wanted to get some advice/suggestions from other here in providing a provision in a 4.16kV Switchgear lineup for connection of a future temporary feeder.
We are providing customer with a switchgear lineup that has a main 4.16kV feed from an upstream transformer and had (3) feeder breakers to downstream loads. The customer has requested that in the event they loose the transformer which feeds this switchgear they want to install a temporary feeder from a nearby transformer to power this gear. This nearby transformer has a dual voltage secondary of both 4.16 & 13.8kV that is selected via tap changer.
Connecting this other feeder to the switchgear properly would require an additional breaker in the switchgear lineup as well as all of the required protection and control (interlocking, transformer diff, bus diff, etc...). The customer does not want to pay for this additional breaker and associated P&C and is simply requesting a landing point provision (lugs or similar) to land these future feeder cables in the event of an emergency. They also do not want to pay for an additional structure to install this landing provision and are suggesting simply adding a set of lugs to the incoming section where the busduct from the normal source transformer comes into the switchgear.
As an OEM and engineer of record I have informed the customer that we cannot provide what they are requesting from a liability standpoint simply overlooking all the P&C that would be required to accomplish this safely and correctly. We have stated that we can provide them with an additional section with bus runbacks labeled for "future bus expansion" or provide them with an additional breaker provision labeled as "future" and what they choose to do with these sections after the switchgear is installed is on them.
Does anyone have any suggestions on how to approach this or see this any differently from a liability standpoint?
We are providing customer with a switchgear lineup that has a main 4.16kV feed from an upstream transformer and had (3) feeder breakers to downstream loads. The customer has requested that in the event they loose the transformer which feeds this switchgear they want to install a temporary feeder from a nearby transformer to power this gear. This nearby transformer has a dual voltage secondary of both 4.16 & 13.8kV that is selected via tap changer.
Connecting this other feeder to the switchgear properly would require an additional breaker in the switchgear lineup as well as all of the required protection and control (interlocking, transformer diff, bus diff, etc...). The customer does not want to pay for this additional breaker and associated P&C and is simply requesting a landing point provision (lugs or similar) to land these future feeder cables in the event of an emergency. They also do not want to pay for an additional structure to install this landing provision and are suggesting simply adding a set of lugs to the incoming section where the busduct from the normal source transformer comes into the switchgear.
As an OEM and engineer of record I have informed the customer that we cannot provide what they are requesting from a liability standpoint simply overlooking all the P&C that would be required to accomplish this safely and correctly. We have stated that we can provide them with an additional section with bus runbacks labeled for "future bus expansion" or provide them with an additional breaker provision labeled as "future" and what they choose to do with these sections after the switchgear is installed is on them.
Does anyone have any suggestions on how to approach this or see this any differently from a liability standpoint?