Hi everyone,
I need some help to determine what my electrical needs are. I hope some of you can share some of your knowledge with me.
I have outgrown my 100 amp 3-phase service, as my computer servers are pulling 2000 watts each continuously and remain at full load 24/7.
I have tried to do basic calculations such as 208x100x1.73 = 35984 watts --> 28787 usable watts to stay at 80% usage of the 100 amp service line.
However I am only able to power nine computer servers (18000w) instead of the projected 14 servers. Am I missing something??
I am using a L5-30 30 amp single phase 208v PDU and the meter is telling me I'm using 17 amps with 2 servers plugged into it. I have 4 of these running.
I found a few new locations that offer 200 amp 208v 3-phase, or 200 amp 480v 3-phase.
My question is:
If I have 200 amp 208v 3-phase service.
1) How many amps would a 3 phase 30 amp (24-derated) PDU pull at full load? 24 amps out of 200 = 176 amps remaining?
Or is it 72 amps out of 200 used, due to 24 amps being used on each Line?
If I have 200 amp 480v 3-phase service..
2) Does that mean I could potentially have 400 amps of 208v service? How would I maximize this to power as many servers as I could safely fit?
I would like to get it right this time and find a location with enough power for me to grow in the future. Thank you for taking the time to provide some advice, it is fully appreciated.
I need some help to determine what my electrical needs are. I hope some of you can share some of your knowledge with me.
I have outgrown my 100 amp 3-phase service, as my computer servers are pulling 2000 watts each continuously and remain at full load 24/7.
I have tried to do basic calculations such as 208x100x1.73 = 35984 watts --> 28787 usable watts to stay at 80% usage of the 100 amp service line.
However I am only able to power nine computer servers (18000w) instead of the projected 14 servers. Am I missing something??
I am using a L5-30 30 amp single phase 208v PDU and the meter is telling me I'm using 17 amps with 2 servers plugged into it. I have 4 of these running.
I found a few new locations that offer 200 amp 208v 3-phase, or 200 amp 480v 3-phase.
My question is:
If I have 200 amp 208v 3-phase service.
1) How many amps would a 3 phase 30 amp (24-derated) PDU pull at full load? 24 amps out of 200 = 176 amps remaining?
Or is it 72 amps out of 200 used, due to 24 amps being used on each Line?
If I have 200 amp 480v 3-phase service..
2) Does that mean I could potentially have 400 amps of 208v service? How would I maximize this to power as many servers as I could safely fit?
I would like to get it right this time and find a location with enough power for me to grow in the future. Thank you for taking the time to provide some advice, it is fully appreciated.