I am in the planning stage of running 800 amps of 480 to a tap box for a new press to be installed. I could use some advice so I don't end up with a bad situation on my hands. The tap box will feed two 400 amp breaker boxes.
I will be doing two 3" emt runs each having (3) 500mcm cables and a ground. The total run will be about 270' with (3) 90's. I plan to place a large J-box about half way.
I am thinking about renting a puller to help out. It is rated at 8000lbs. Does anyone know what this unit can easily handle? I mean, is it too much to try and do the entire 270' in a single pull?
If that is too much to expect, I will probably go old school and pull it with a sleeve pully and the forklift from the J-box. I don't see a good way to use the lugger with a ceiling mounted J-box. It is a 25' ware house ceiling.
Two other questions: What is the correct size ground conductor for these runs?
I know wire must be equal length, but to what sort of accuracy? Are we talking within a foot or two, or down to a fraction of an inch?
I will be doing two 3" emt runs each having (3) 500mcm cables and a ground. The total run will be about 270' with (3) 90's. I plan to place a large J-box about half way.
I am thinking about renting a puller to help out. It is rated at 8000lbs. Does anyone know what this unit can easily handle? I mean, is it too much to try and do the entire 270' in a single pull?
If that is too much to expect, I will probably go old school and pull it with a sleeve pully and the forklift from the J-box. I don't see a good way to use the lugger with a ceiling mounted J-box. It is a 25' ware house ceiling.
Two other questions: What is the correct size ground conductor for these runs?
I know wire must be equal length, but to what sort of accuracy? Are we talking within a foot or two, or down to a fraction of an inch?