Hello and thanks in advance I have Mostly industrial experience and have been ask by a good friend to help with the installation of a sub panel in a 60 X 80 attached addition on to his Diesel/semi repair facility I will outline the situation then list my questions below that. Thanks in advance
60 X 80 attached addition on to his Diesel/semi repair facility
100 AMP sub panel
He has plenty of capacity to feed the sub panel from two 200AMP distribution panels in his existing shop
Distance from two 200AMP distribution panels to new sub panel is 110 feet
the loads on the new sub panel are as follows
20) 4 foot led lights ( 5 rows of 4)
20) Duplex receptacles
2) outdoor lights
4) welder receptacles
2) exit lights
QUESTIONS
1) Is #1 copper the correct size for the feeder wires ?
2) Should the feeder wires be 4 conductors with down sizing the ground one size to a #2 ok?
3) should Ground and neutral be isolated in sub panel
4) should there be grounding rod(s) installed at sub panel? 1 or 2 ?
5) Should all 120 V receptacles be on GFCI breakers ?
6) there is only one welder in shop can we install 4 welder (50 AMP) receptacles on one circuit (will more than likely install 2 per circuit)
7) Should the welder breaker be a GFCI?
8) Can someone recommend a good choice for the Led lights ? Ceiling height 18 feet. Would also like two lights with motion detection for each entry door.
9) can someone recommend a good outdoor light to install one on each end of the building at the peak (25 to 30 ft) to really provide good lighting to detour loitering and theivery
Thanks again this is a great site !
60 X 80 attached addition on to his Diesel/semi repair facility
100 AMP sub panel
He has plenty of capacity to feed the sub panel from two 200AMP distribution panels in his existing shop
Distance from two 200AMP distribution panels to new sub panel is 110 feet
the loads on the new sub panel are as follows
20) 4 foot led lights ( 5 rows of 4)
20) Duplex receptacles
2) outdoor lights
4) welder receptacles
2) exit lights
QUESTIONS
1) Is #1 copper the correct size for the feeder wires ?
2) Should the feeder wires be 4 conductors with down sizing the ground one size to a #2 ok?
3) should Ground and neutral be isolated in sub panel
4) should there be grounding rod(s) installed at sub panel? 1 or 2 ?
5) Should all 120 V receptacles be on GFCI breakers ?
6) there is only one welder in shop can we install 4 welder (50 AMP) receptacles on one circuit (will more than likely install 2 per circuit)
7) Should the welder breaker be a GFCI?
8) Can someone recommend a good choice for the Led lights ? Ceiling height 18 feet. Would also like two lights with motion detection for each entry door.
9) can someone recommend a good outdoor light to install one on each end of the building at the peak (25 to 30 ft) to really provide good lighting to detour loitering and theivery
Thanks again this is a great site !