AFCI and residential elevator

Status
Not open for further replies.

BArmy

Member
Location
Jackson Wy
Occupation
inspector
The lighting circuit for the cab lights in an residential elevator (single family dwelling) AFCI requirements apply? The hall ways and entry ways are under 210.12. What do you think the code says on this?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
210.12 Arc-Fault Circuit-Interrupter Protection. Arc-fault
circuit-interrupter protection shall be provided as required in
210.12(A), (B), and (C). The arc-fault circuit interrupter shall
be installed in a readily accessible location.
(A) Dwelling Units. All 120-volt, single-phase, 15- and 20-
ampere branch circuits supplying outlets or devices installed in
dwelling unit kitchens, family rooms, dining rooms, living
rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, laundry areas, or similar rooms or

areas shall be protected by any of the means described in
210.12(A)(1) through (6):

I don't see elevator listed here.
 